Thread Links | Date Links | ||||
---|---|---|---|---|---|
Thread Prev | Thread Next | Thread Index | Date Prev | Date Next | Date Index |
Mike, I disagree that my observations rely on the
portion of optics in the SONET/SDH market. I am simply using the SONET/SDH
application data to illustrate that short-reach SM optics comprise only a small
fraction of the total SM optics for SONET/SDH. I then apply this observation
to Ethernet application space. As a result, the 4% allocation I suggested as a
default grant to Ethernet SM optics in data centers is likely generous for two
reasons. 1) I suspect that the portion of short-reach SM optics would be
higher for SONET/SDH than for Ethernet because SM optics are more preferred by
carriers, the primary users of SONET/SDH, than by enterprise customers, and 2)
the short-reach optics in this bin in the barbieri contribution include both
2km and 7km variants, only a fraction of which would actually be deployed in COs
or DCs. Some would be deployed between I also disagree that the ratio of 10G-LR
to 10G-SR is a good grant to SM deployments in DCs at any data rate. On one hand,
while I have not tried to employ the data details from the barbieri reference to
hone this analysis, a grant larger than 4% during the early phase of deployment
might be more reasonable given that this data shows that historically SM optics
are deployed earlier than MM. On the other hand, a 20% grant as the
application reaches maturity is the same as saying all SM deployments are in
DCs and none are in spaces outside DCs, which is obviously way off. Further, the
cost disparity favoring MM optics at 100G is far higher than at 10G which would
tend to skew even the early 100G deployments towards MM. This disparity is very
real and causing market acceptance barriers today. To conclude, I cannot see justification
for LR4 grants. However, a grant of a few percent might be reasonable for SM
variants that close the cost disparity to something similar to that observed
between 10G-LR and 10G-SR. But if such a grant is applied to SM optics, then a
grant should also be applied to MM optics over lower capability options like
copper. From where I stand today such fine tuning is not worth the effort given
the elevated risk of analysis paralysis that accompanies it. Regards, Paul From: It looks as though I
mis-interpreted the numbers. I would point out however that
your argument is relying on the fact that the SONET/SDH is a significant
proportion of the overall market. If it is not then the percentage
of these links that are less than 7km is irrelevant. I believe the
best number to use for this analysis would be the ratio between useage of
10GBASE-LR modules and 10GBASE-SR modules. I would be surprised if
it is only 4%. QLogic Corporation Senior Manager
Signal Integrity Aliso 949 389 6269 -
office. Mike.Dudek@xxxxxxxxxx From: Mike, You make good observations. But
please note that the ~80/20 split includes all usage not just within a data
center. The barbieri reference cited below also shows on slide 9 that for
SONET/SDH the percentage of sub 7km SM optics deployed is less than 20% of the
overall SM mix. And this is for an application that sees much less MM
deployment compared to Ethernet. So while I think your argument has
validity, the ratios may need adjustment. Instead of assuming 20% SM
ports in DCs, the SONET/SDH data suggests that it may be more accurate to
assume less than 1/5th of this (< 4%) of the total SM ports are
in DCs. So rather than 20% + 0.8*(SM coverage), it may be better to use
4% + 0.96(SM coverage). Paul From: On the topics of
volume I think we need to be clear that the 20% SMF to 80% MMF is not a fixed
ratio. I think that the ratio should be mainly explainable by
the capabilities of the units. At the moment the MMF is sufficiently
lower cost than SMF that within the data center most installations use MMF when
they can and SMF when MMF hasn’t got the reach. If the MMF
reach becomes shorter it’s volume will drop and the SMF volume will
increase. That is evident in Paul’s spreadsheet (and is I think one
of the basic assumptions in his spreadsheet). Looking at that
spreadsheet however there is obviously some additional usage for SMF at 10G
because if one puts 300m for the multimode solution it predicts that the SMF
percentage is well less than 2%. Based on this I think
we could assume that the SMF percentage will be approximately 20% + .8*(SMF
percentage from Paul’s spreadsheet) while the MMF percentage will be .8*(MMF
percentage from Paul’s spreadsheet.). As an example if
one assumes the following: MMF reach is dropped
to 75m there are equal
numbers of server to switch links using fiber and switch to switch links the switch to switch
links use a 2:1 ratio for the single versus double-link Paul’s spreadsheet
would predict that in his population there is only a 16.4% single mode
usage. That would change the overall ratio to 33% SMF to 67%
MMF. Adding an additional
lower cost shorter distance SMF spec would however complicate the
analysis. The big question would be how much of the 20% additional
SMF market would go to the lower cost shorter distance spec. If a large
percentage does then the volume of the LR4 would drop potentially increasing
its cost substantially. QLogic Corporation Senior Manager
Signal Integrity Aliso 949 389 6269 -
office. Mike.Dudek@xxxxxxxxxx From: David, Thanks for your efforts on this fundamentally important topic, going so
far at to involve the governing authority of IEEE for guidance and reassurance
of the current practices. While I still believe that the current practice
is overly restrictive, I also appreciate the line that may be crossed if
discussions stray to far afield on the topic of price. I intend to abide
by the guidance you have given. All, With regard to translation between cost and price, there are several
forces at work. I previously mentioned the gorilla in the room.
There is also the equally important factor of production rate, for increased
volumes often translate into decreased costs. The comparison of cost must
be couched in terms of volume, for it can be imbalanced to compare input costs
of different proposals if they are stated with expectation of differing
volumes. I urge all contributions on costs to also provide them in the
context of their volume assumptions. We must also realize that if volume
context is given in terms like “at equivalent volumes of X”, where X is volume
of a baseline technology that is well along its maturity curve, such volumes
for 100G technologies may be many years into the future. Therefore a
large gap may exist between present costs and distant future cost
potential. We must also remember to consider the fact that historically
the market demand for our optical solutions tends to fall along an 80/20 rule,
with 80% of the port volumes going to multimode and 20% going to single-mode.
See http://www.ieee802.org/3/hssg/public/nov06/barbieri_01_1106.pdf So we must be weary of using the volumes of multimode solutions as the
volume basis for cost projections of proposed single-mode solutions unless
those single-mode solutions are presumed to replace multimode solutions and not
just augment them in data centers. The above contribution also provides historical adoption rates of
single-mode solutions by reach that can set context for expectations.
Regards, Paul -----Original Message----- Hi Paul, I want to bring your attention to the text 'Discussion of the cost of
inputs necessary to create a compliant implementation of a standard are treated
differently from discussions of prices at which compliant implementations can
or should be sold. There is no useful or appropriate reason to discuss selling
prices of implementations - each implementer of the standard should use its own
independent business judgment to make that decision. In contrast, there is a
legitimate reason to discuss costs of inputs used in implementation.'. I believe this agrees with your point that the information is
publically available - but states 'There is no useful or appropriate reason to
discuss selling prices of implementations' which I believe is what you are
requesting. If a discussion of current and past end user cost (price) of products
that implement the standard were to occur it could very easily stray into a
discussion of the future end user costs of the proposed standard, which you
agree is not allowed. This is addressed in the answer to the question 'So is it
okay to talk about prices or output levels in an IEEE-SA meeting as long as we
don’t reach an agreement?' which states: No, it’s not okay. First, you can’t always control where the discussion
will go – it may end up in undesired areas. Second, if agreeing on the subject
would be unlawful (such as the respective selling prices of compliant
products), then that subject should not be discussed. And third, it’s not up to
you to decide whether your words and conduct amount to an agreement – in the I have discussed your concerns with David Ringle, Director, Governance
& Technical Committee Programs at the IEEE-SA, and he is in agreement with
my position. Best regards, David _______________________________________ From: Sent: 17 November 2011 17:22 To: Subject: Re: [802.3_100GNGOPTX] Emerging new reach space David, Thanks for the pointers to the IEEE policy. I have been reviewing
it and find the following particularly relevant to the thread below. I
have underlined key parts for easier reference. What else can we discuss? IEEE wants you to have the maximum
flexibility to discuss topics relevant to developing a standard while also
adhering to certain rules designed to minimize risk. It is impossible to
identify all the topics that you can discuss, but here are some that you cannot
discuss: • prices at which products or services implementing the standard should
be sold (“price” includes discounts, terms, and other conditions of sale); • profits or profit margins; • individual companies’ market shares or sales territories; • allocation of customers, markets, production levels, or territories;
or restricting the customers to whom, or territories in which, a company may
sell or resell products; • using standards or certification programs to exclude suppliers or
competitors from the marketplace for any reason other than cost-performance or
technical considerations; • conditioning the implementation of a standard on the implementer’s
use of products or services from a particular supplier [such as requiring use
of a particular manufacturer’s components or requiring implementers to use a
particular service provider(s) for compliance certification]; • bidding (or terms of bids) or refraining from bidding to sell any
product or service; • any matter which restricts any company’s independence in setting
prices, establishing production and sales levels, choosing the markets in which
it operates, or the manner in which it selects its customers and suppliers. The first bullet gets at the heart of the matter. It is what
everyone keys on when the discussions of price are thwarted. It states we
cannot discuss what prices should be. I think we can all agree that to do
so would be anti-competitive. But it says nothing about discussions of
prices as they actually are in the market today or have been in the past.
To muzzle such discussions is overstepping the bounds and scope of the policy,
for there is no anti-trust reason why prices that are in public domain, such as
can be found posted on public web sites, cannot be brought forward. Such
activity is not price fixing, it is price reporting. In the case of setting new standards we are naturally talking about
documents that affect the future. This is the context under which the
IEEE policy is written and should be interpreted and applied. When the
policy says: Discussion of the cost of inputs necessary to create a compliant
implementation of a standard are treated differently from discussions of prices
at which compliant implementations can or should be sold. There is no useful or
appropriate reason to discuss selling prices of implementations – each
implementer of the standard should use its own independent business judgment to
make that decision. In contrast, there is a legitimate reason to discuss costs
of inputs used in implementation. … With regard to the costs of inputs used in implementing a standard, the
only permitted discussion is the degree to which such costs may differ.
Examples of permissible discussion topics would include differences in
comparative component costs, operating costs, licensing costs, or the aggregate
of such costs. The importance of this restriction on discussion is reinforced
by the understanding that participants in the development of a standard often
come from multiple stages of the supply chain (e.g., the input cost of a
component to a system manufacturer is the output price of a component
supplier). Thus, in standards development technical activities, participants may
discuss the relative costs (in terms, for example, of percentage increases or
decreases) of different proposed technical approaches in comparison with the
relative technical performance increases or decreases of those proposals. It is obviously referring to the setting of new standards. This
is conveyed by the use of the word “proposed” and more fundamentally by the
entire context of the policy for guiding standards development. While it
is not referring to discussions of cost for implementations already standardized
and in the market, the above restrictions are needlessly being applied that
way. There is no anti-trust implication to discussions of publicly
available information, even if it is with regard to price. How can there
be? It’s already fully available to all participants. Such restrictions
would imply that discussions of current prices somehow set agreements on future
prices of yet-to-be-standardized implementations. That is a
non-sequitur. If we are talking about input costs on items affecting the setting of
future standards, the guidelines are clear that we must use relative costs, not
absolute costs. It also recognizes the supply chain issue, that one link’s cost is the
previous link’s price. But it places no restriction on the point in the
supply chain at which relative costs can be compared. Therefore
imposition of restrictions on discussions of relative costs at the top of the
supply chain or any other specific part of the supply chain is outside of this
policy. While I do not relish raising these issues, I feel compelled to do so
because after reading the actual policy it is clear to me that our practices in
802.3 are unnecessarily restrictive both to the letter and spirit of the IEEE
policy. Regards, Paul -----Original Message----- From: Law, David [mailto:dlaw@xxxxxx] Sent: Thursday, November 17, 2011 8:02 AM To: Subject: Re: [802.3_100GNGOPTX] Emerging new reach space Hi Jonathan, While I note that Dan has already stated that comparing cost at the end
user is not permitted, and discussion did not go into that area, I wanted to
reiterate that such discussion are not permitted. I also wanted to respond to
your request to me to comment. As I have often stated at meetings, I would encourage everybody to read
the IEEE policy document 'Promoting Competition and Innovation: What You Need
to Know about the IEEE Standards Association’s Antitrust and Competition
Policy' <http://standards.ieee.org/develop/policies/antitrust.pdf>. I
personally think it provides a good explanation of why these rules are in
place, due to the Antitrust and competition laws throughout the world, and the
consequences if they are not followed. This policy states that we cannot discuss, among other items, 'prices
at which products or services implementing the standard should be sold (“price”
includes discounts, terms, and other conditions of sale)'. This is enforced in
subclause 5.3.10.3 'Discussion of relative cost/benefit analyses' of the
IEEE-SA Standards Board Operations Manual and stated in the 'Guidelines for
IEEE-SA Meetings' slide shown at every meeting. By way of an introduction to why these rules are in place, and the
consequences to all of us if they are not followed, I offer the following extract
from the introduction to the above policy document. Clause 2 of this document
addresses 'Cost Discussions' in further detail. Participants may also wish to
consult 'What You Need to Know About IEEE Standards and the Law'
<http://standards.ieee.org/develop/policies/stdslaw.pdf>. ---- Promoting Competition and Innovation: What You Need to Know about the
IEEE Standards Association’s Antitrust and Competition Policy Antitrust and competition laws throughout the world rest on the premise
that competition in the provision of products and services is the best way to
ensure that consumers and other users receive maximum innovation and quality at
the lowest possible prices. But sometimes effective competition requires a
measure of cooperation among competing firms. Standards development is one of those areas. Standards development
serves one part of the IEEE’s mission – advancement of global prosperity by
fostering technological innovation – but it can do so only if the standards
development is conducted consistent with the antitrust and competition laws
that regulate the nature and extent of cooperation in which competitors can
legitimately engage. The IEEE-SA is an international membership organization that provides a
standards program serving the global needs of industry, government, and the
public. A violation (or claims of violation) of competition laws will
jeopardize what all participants are working so hard to build; will impede the
IEEE mission; and may expose participants and their employers to the risk of
imprisonment and other criminal penalties, civil remedies, and significant
litigation costs. Even if a competition-law case or investigation is ultimately
dropped, that will often happen only after the parties have spent considerable
resources in responding to information requests and defending against the
claims. The IEEE-SA wants to help all of its participants avoid competition-law
problems. Many IEEE-SA participants receive antitrust/competition-law
compliance training from their employers, and IEEE-SA participants should
always consult with their own or their company counsel when they have
competition-law-related questions. This brochure is not intended to replace
that competition-law training, advice, or other competition-law-related
resources that participants may have available to them; rather, this brochure
is intended to highlight the competition-law risks that are most pertinent to
standards development and to explain the IEEE-SA’s policies with respect to
competition law matters. <http://standards.ieee.org/develop/policies/antitrust.pdf> ---- Best regards, David ________________________________________ From: Sent: 16 November 2011 20:04 To: Subject: Re: [802.3_100GNGOPTX] Emerging new reach space Hi Robert, I am not sure its even appropriate to comment about prices-of-resale.
Its a topic better left understood without discussion within the IEEE. We all
have a general idea of the challenges we face in assessing relative cost. In my opinion, you do it by looking at fundamental architectural
components and their specifications. You do it by looking at cost from a
form/fit/function perspective and leave out things like market pricing, demand
or volume. You choose *cost* comparisons with components that have equivalent
markets/volumes and then your comparison can have merit without getting into
the esoteric aspects of the market. Dan From: Robert Lingle <rlingle@xxxxxxxxxxxxx> Reply-To: Robert Lingle <rlingle@xxxxxxxxxxxxx> Date: Wed, 16 Nov 2011 22:52:26 +0000 To: 100G Group < Subject: Re: [802.3_100GNGOPTX] Emerging new reach space Jonathon, I agree with your former sentiment about it being against IEEE
guidelines, so we must not do it. I am sure Paul agrees. However I don’t agree with the latter sentiment. I think Paul is
pointing out a real quandary in our task. I think we can point out cases where
the adoption of components has been substantially impacted by the
prices-of-resale, over a lengthy period of time. I am not sure how long we
would have to wait for the long term? It seems to be a genuine difficulty in carrying out the analysis we all
want to see. I don’t have a solution. Warm regards, Robert From: Jonathan King [mailto:jonathan.king@xxxxxxxxxxx] Sent: Wednesday, November 16, 2011 5:15 PM To: Subject: Re: [802.3_100GNGOPTX] Emerging new reach space Hi Paul, I cannot support comparing cost at the end user, because
(in my opinion) that is quite clearly a price, and would be contrary to IEEE
guidelines. I would like David Law to weigh in on this. In an efficient market economy, the cost of manufacture (not the cost
of distribution) of a product, or group of products, is the best indicator for
long term cost to the end user. I think that’s what we (802.3) want to
get some indicator of when striving for ‘low cost’ solutions. Best wishes Jonathan From: Sent: Tuesday, November 15, 2011 8:30 PM To: Subject: Re: [802.3_100GNGOPTX] Emerging new reach space I also like Jack’s perspective foundation. And I have to agree
that a common small port form factor would be valuable. Regarding the PMD cost comparisons, I also agree that picking a common
cost basis could eliminate translation problems that come with use of different
bases. For PMD relative costs I am fine with choosing either 10GE SR or
LR because I don’t quite appreciate Chris’ concerns over the danger in using LR
as the basis. But if there is a problem, it seems like it could be
avoided by eliminating the bit/sec factor and instead using simple cost. However, there is still the issue of picking the point in the supply
chain at which the baseline cost is chosen. It could be at the level of
the transceiver manufacturer, or up one level to the switch manufacturer, or
off on another branch to distributors, or up one level again to the end
user. There can be substantial differences in these costs, which is what
likely gives rise to the “order of magnitude” perception disparity that Chris
mentioned. While we are forbidden to talk about it, it is the 500 pound
gorilla in the room. In some cases it tips the scales lightly and in
other cases it leans its full weight. Yet this weight is what is creating
a 100GE market acceptance barrier in data center deployments. While there is clear cost reduction potential in reducing the multimode
lane count based just on the improvement in media cost, the benefit of defining
a new single-mode solution may depend largely on the gorilla, for if we go to a
parallel solution the media will only get more costly. So for me the
biggest cost question is whether defining a new single-mode solution moves the
gorilla from leaning heavily to leaning lightly. While I’d like to agree to use cost at the transceiver maker level as
the basis, it cannot address this big question. If used it will likely
result in highly distorted perceptions and projections because it ignores the
order-of-magnitude problem. The only point in the supply chain where
transceiver costs and cabling costs come together is at the end user
level. This dilemma is hitting me squarely as I try to further my work on
the “Kolesar_Kalculator”. I continue to wonder what good this tool
will do if the PMD cost and cable cost are in two different silos without a
common basis to bring them together, for it is the combination of the two that
defines the total channel cost that we must optimize. I need to find a
way to appease the gorilla. If only Fay Wray were here… ________________________________________ From: Chris Cole [mailto:chris.cole@xxxxxxxxxxx] Sent: Tuesday, November 15, 2011 7:33 PM To: Subject: Re: [802.3_100GNGOPTX] Emerging new reach space Hello Jack, Nice historical perspective on the new reach space. Do I interpret your email as proposing to call the new 150m to 1000m
standard 100GE-MR4? ☺ One of the problems in using today’s 100GE-LR4 cost as a comparison
metric for new optics is that there is at least an order of magnitude variation
in the perception of what that cost is. Given such a wide disparity in
perception, 25% can either be impressive or inadequate. What I had proposed as reference baselines for making comparisons is
10GE-SR (VCSEL based TX), 10GE-LR (DFB laser based TX) and 10GE-ER (EML based
TX) bit/sec cost. This not only allows us to make objective relative
comparisons but also to decide if the technology is suitable for wide spread
adoption by using rules of thumb like 10x the bandwidth (i.e. 100G) at 4x
the cost (i.e. 40% of 10GE-nR cost) at similar high volumes. Using these reference baselines, in order for the new reach space
optics to be compelling, they must have a cost structure that is referenced to
a fraction of 10GE-SR (VCSEL based) cost, NOT referenced to a fraction of
10GE-LR (DFB laser based) cost. Otherwise, the argument can be made that
100GE-LR4 will get to a fraction of 10GE-LR cost, at similar volumes, so why
propose something new. Chris From: Sent: Tuesday, November 15, 2011 3:06 PM To: Subject: [802.3_100GNGOPTX] Emerging new reach space Following last week's meetings, I think the following is relevant to
frame our discussions of satisfying data center needs for low-cost low-power
interconnections over reaches in the roughly 150-1000m range. This is a
"30,000ft view,"without getting overly specific. Throughout GbE, 10GbE, 100GbE and into our discussions of 100GbE
NextGenOptics, there have been 3 distinct spaces, with solutions optimized for
each: Copper, MMF, and SMF. With increasing data rates, both copper and MMF
specs focused on maintaining minimal cost, and their reach lengths decreased.
E.g. MMF reach was up to 550m in GbE, then 300m in 10GbE (even shorter reach
defined outside of IEEE), then 100-150m in 100GbE. MMF reach for 100GbE
NextGenOptics will be even shorter unless electronics like EQ or FEC are
included. Concurrently, MMF solutions have become attractive over
copper at shorter and shorter distances. Both copper and MMF spaces have
"literally" shrunk. In contrast, SMF solutions have maintained a 10km
reach (not worrying about the initial 5km spec in GbE, or 40km solutions). To
maintain the 10km reach, SMF solutions evolved from FP lasers, to DFB lasers,
to WDM with cooled DFB lasers. The 10km solutions increasingly resemble
longer-haul telecom solutions.! There is an increasing cost disparity between MMF and SMF
solutions. This is an observation, not a questioning of the reasons behind
these trends. The increasing cost disparity between MMF and SMF solutions is
accompanied by rapidly-growing data center needs for links longer than MMF can
accommodate, at costs less than 10km SMF can accommodate. This has the
appearance of the emergence of a new "reach space," which warrants
its own optimized solution. The emergence of the new reach space is the crux of
this discussion. Last week, a straw poll showed heavy support for "a PMD supporting
a 500m reach at 25% the cost of 100GBASE-LR4" (heavily favored over
targets of 75% or 50% the cost of 100GBASE-LR4). By heavily favoring the most
aggressive low-cost target, this vote further supports the need for an
"optimized solution" for this reach space. By "optimized
solution" I mean one which is free from constraints, e.g. interoperability
with other solutions. Though interoperability is desirable, an interoperable
solution is unlikely to achieve the cost target. In the 3 reach spaces
discussed so far, there is NO interoperability between copper/MMF, MMF/SMF, or
copper/SMF. Copper, MMF and SMF are optimized solutions. It will likely take an
optimized solution to satisfy this "mid-reach" space at the desired
costs. To repeat: This has the appearance of the emergence of a new
"reach space," which warrants its own optimized solution. Since the
reach target lies between "short reach" and "long reach,"
"mi! d reach" is a reasonable term Without discussing specific technical solutions, it is noteworthy that
all 4 technical presentations last week for this "mid-reach" space
involved parallel SMF, which would not interoperate with either 100GBASE-LR4,
MMF, or copper. They would be optimized solutions, and interest in their
further work received the highest support in straw polls. Given the
high-density environment of datacenters, a solution for the mid-reach space
would have most impact if its operating power was sufficiently low to be
implemented in a form factor compatible with MMF and copper sockets. Cheers, Jack |