I am picking up on a thread that is about 10 days old.  I have changed the “Subject:” to better identify the contents for future reference.  

 

To restate, the crux of the issue is to define a power budget that is useful for data center environments.  For single-mode channels in data centers the attenuation of the fiber consumes a minor fraction of the loss needed to properly support useful channel topologies, with a far larger fraction of the loss budget devoted to overcoming connection insertion loss.  The bulk of what follows is therefore devoted to determining the connection loss budget.

 

Since the writing of the thread below, a few of us have been exchanging thoughts on establishing loss budgets for potential new single-mode solutions.  We have been taking into account the need to support at least a 500 m reach and sufficient numbers of patch panels to support double-link channels made of structured cabling.  We also recognize that there is a fundamental difference between the number of connections within a 2-fiber channel and a parallel fiber channel, as depicted in the diagram below.  In this diagram the foreground channel requires 4 MPOs to support a parallel fiber solution.  The background channel requires 4 MPOs plus 4 LCs because of the use of fan-out cassettes commonly deployed for pre-terminated cabling.  

 

 

 

During our private discussions a contribution by Jonathan King to P802.3ba, king_01_0508, was referenced as a way to approach the problem of connection loss allocation.  In his work Jonathan modeled multimode MPO connection loss with a Rayleigh distribution using Monte Carlo techniques to derive a proposal for power budget allocation.  In the tabulation just below I have used the same mean and standard deviation that Jonathan proposed, but applied Normal statistical formulae for comparison.  The trends in Jonathan’s Monte Carlo results closely track those for Normal distribution formulae, even though Jonathan’s loss distributions are Rayleigh rather than Normal.  Here is a side by side comparison.

 

# conn  JK’s Monte Carlo           Normal Stat Calc

            mean    std.dev.             mean    std.dev.

1          0.22      0.134                0.22      0.134

2          0.421    0.187                0.44      0.190

3          0.631    0.221                0.66      0.232

4          0.842    0.264                0.88      0.268

 

The means and standard deviations of the two approaches agree to within 5%, with the Normal statistical approach being slightly more pessimistic.  I bring this up because it shows one can apply other methods and get similar answers, which is a good cross-check as well as opening another analytical degree of freedom which I will employ for single-mode connections below. 

 

However, it is not clear if Jonathan’s simulation properly accounts for the fact that connection loss does not increase linearly with lateral offset.  In other words, it accelerates with increasing offset.  So while pure Rayleigh distributions are good for modeling offsets, properly converting them to compute loss has the effect of progressively stretching the distribution towards higher loss, increasing the mean and the standard deviation.  I’ll put this aside, opting for keeping it simple for now, knowing that the statistical calculations I use below help to account for this.  

 

If we accept Jonathan’s premise that 1.5 dB is sufficient to support 4 multimode MPO connections with a resulting failure rate of 1.6% (i.e. see page 11 where loss exceeds 1.5 dB for 1.6% of the connections), then that can be applied as a benchmark for this work too.  In his simulation this represents the +2.5 standard deviation point in the distribution (mean + 2.5*std.dev. = 1.5 dB).  For the normal statistical calculations this represents the +2.3 standard deviation point. 

 

Now all we need to quickly calculate the loss (i.e. without M.C. simulation) is the mean and standard deviation for single-mode 2-fiber connections and array connections.  But determining these values is not trivial.  If you search the web you can find a variety of performance claims, stated with different terminology like typical, average, maximum, and sometimes mean and standard deviation.  What’s even more confounding is that these specs are stated under differing conditions, such as random mate to like product, when mated to a reference-grade plug, or when “tuned” (or various combinations of these).  Tuning is the process by which a cylindrical ferrule is iteratively clocked into optimal performance position, a labor intensive process.  The bottom line is that one can argue about specs from many different angles, each one backed up by some evidence.  I wish to cut thru all that and get down to what will work in practice for cabling that is commonly deployed in data centers.  So here goes.

 

Connections should be modeled using random mate statistics for un-tuned assemblies because random mate concatenations represent actual deployment conditions and un-tuned terminations are lower in cost and commonly used in data center environments.  A good starting point for single-mode LCs and SCs is mean = 0.2 dB, standard deviation = 0.15 dB.  A good starting point for single-mode MPOs is mean = 0.35 dB, standard deviation = 0.25 dB.  Using these values, the statistical calculation for 2.3 standard deviations of four LCs/SCs plus four MPOs is 3.54 dB.  For four MPOs alone it’s 2.55 dB.  Add fiber attenuation at a rate of at least 0.5 dB/km to account for the use of indoor cabling (as opposed to outside plant’s ~0.4 dB/km) and you have a useful solution.  

 

As an aside, TIA’s attenuation specs for single-mode cable at 1310 and 1550 nm are:

1.0   dB/km for indoor plant

0.5 dB/km for indoor/outdoor

0.5 dB/km for outside plant.

These are commonly used as the performance limits for structured cabling. Up to this point in the evolution of single-mode systems defined for 802.3, the use of OSP specs from ITU have made sense because they were focused on distances that were clearly meant to support outside plant in the network.  But the continued use of ITU specs is not a wise choice for data center environments (i.e. primarily indoor with some mix of indoor/outdoor deployment) where TIA and ISO structured cabling standards prevail.    

 

To summarize, the minimum loss budgets that I think are needed to well support 500 m channels are these:

~2.8 dB for parallel fiber solutions,

~3.8 dB for 2-fiber solutions.  

 

For reference, the LR4 loss budget is 6.3 dB, so the above values represent 44% of the LR4 budget (3.5 dB lower) and 60% of the LR4 budget (2.5 dB lower) respectively.  These are substantial reductions that should allow lower cost solutions.  However, if the budgets are trimmed further they will loose utility and the IEEE effort will be in vein.  This would be the case if we followed 802.3’s prior approach of allocating only 2 dB of connection and splice loss for the channel.  As previously mentioned, this has worked for data centers in the past only because there is ample remaining loss budget to put in place to overcome the attenuation of long lengths of fiber, typically at least 4 dB to support 10 km.  In these past cases, for shorter channels the fiber attenuation budget is routinely traded for extra connection insertion loss budget.  We will not have that luxury within the short-reach budgets we are considering.  Also it should be noted that the 3.8 dB value for 2-fiber solutions is not far from the usual 4 dB loss budget commonly provided for short-reach central office solutions.  

 

Hopefully this discussion (really an on-line presentation) will help us converge our concepts for next week’s meeting.

 

Regards,

Paul

 

 

From: Chris Cole [mailto:chris.cole@xxxxxxxxxxx]
Sent: Tuesday, January 08, 2013 1:55 PM
To: STDS-802-3-100GNGOPTX@xxxxxxxxxxxxxxxxx
Subject: Re: [802.3_100GNGOPTX] SMF Ad Hoc

 

Paul,

 

The way to derive a link budget for structured data center cabling is as you articulate below. This works well for optics intended for structured cabling applications, for example MMF SR and SR4 and the new SMF minimum 500m interface.


The does not work for applications where the assumptions you make are not valid.

 

Chris

 

From: Kolesar, Paul [mailto:PKOLESAR@xxxxxxxxxxxxx]
Sent: Tuesday, January 08, 2013 1:48 PM
To: STDS-802-3-100GNGOPTX@xxxxxxxxxxxxxxxxx
Subject: Re: [802.3_100GNGOPTX] SMF Ad Hoc

 

Scott and Chris,

The crux of the issue is to define a power budget that is useful for data center environments.  For single-mode channels in data centers the attenuation of the fiber consumes a minor fraction of the loss needed to properly support useful channel topologies, with a far larger fraction of the loss budget devoted to overcoming connection insertion loss.  

 

There can be a significant difference in what is needed to support 2-fiber channels compared to parallel channels for the same topology.  This is because, for pre-terminated structured cabling, there are twice as many connections for 2-fiber channels owing to the deployment of fan-out cassettes that transition from array connections (e.g. MPOs) on the permanent link cabling to multiple 2-fiber appearances (e.g. LCs or SCs) on the front of the patch panel.  For parallel solutions these fan-out cassettes are not used because the fan-out function is not needed.  Instead, array equipment cords attach directly to array pre-terminated permanent link cabling.  Thus parallel solutions deploy only array connections, one at each patch panel appearance, while 2-fiber solutions employ a 2-fiber connection plus an array connection at each patch panel appearance.  

 

For the long data center channels that single-mode systems are expected to support, two-link (or greater) topologies will be very prevalent.  A two-link channel will present four patch panel appearances, one on each end of the two links.  For 2-fiber transmission systems, that means we need enough power to support four 2-fiber connections plus four array connections, a total of eight connections.  For parallel transmission systems, that means we need enough power to support four array connections. 

 

To show an example, I’ll take a simple approach of allocating 0.5 dB per connection.  This translates into a need to provide 4 dB of connection loss for 2-fiber systems and 2 dB for parallel systems.  Admittedly this isn’t correct because, among other things, 2-fiber connections generally produce lower insertion loss than array connections. But it serves to illustrate that the difference in useful loss budgets between the two systems can be significant, being associated with the loss allocation for four 2-fiber connections.  

 

In prior 802.3 budgets we typically allocated 2 dB for connection loss in single-mode channels.  However, in the past the length of fiber was much longer, typically at least 10km.  This meant that at least 4 dB of power was devoted to overcome fiber attenuation.  For such systems it is possible, and quite typical, to exchange the fiber loss allocation for additional connection loss when the channel is short.  So 10km budgets supported the above structured cabling scenario.  For P802.3bm we are talking about supporting much shorter channels, so the fiber loss allocation will be much smaller making such trade-off no longer very helpful.  But the customer still needs to support channels with at least two links.  

 

The bottom line is that a blanket absolute connection loss allocation is not the best approach.  Rather we should be requiring support for a minimum number of patch panels, which I propose to be four for the two-link channel.  From this the number of connections will depend on the system, and the connection loss allocation can be appropriated accordingly.  

 

Hopefully this helps draw the disparate views together.  

 

Regards,

Paul

 

 


From: Chris Cole [mailto:chris.cole@xxxxxxxxxxx]
Sent: Tuesday, January 08, 2013 12:06 PM
To: STDS-802-3-100GNGOPTX@xxxxxxxxxxxxxxxxx
Subject: Re: [802.3_100GNGOPTX] SMF Ad Hoc

 

Scott


I disagree.

 

For structured links, as explained to us by Paul Kolesar, the number of connections is known, for example 2 for single-link channels and 4 for double-link channels (kolesar_02_0911_NG100GOPTX). This works well when defining MMF link budgets, for example SR or SR4, and also the proposed new 500m SMF standard, which can be viewed as a reach extension of the 100m or 300m MMF application space.

 

However, that is not how 2km or 10km SMF interfaces are used. These have a variable number of connections and often include loss elements. It is reasonable as a methodology to start out with a nominal number of connections and fiber loss to determine a starting point link budget. However, it is unreasonable to stop there and ignore widespread deployment. So using the methodology outlined below to determine a 2km loss budget gives the wrong answer.


The right answer is arrived at by looking at what is widely deployed, what works for end users, and what end users who are not optics engineers implicitly expect from a 2km interface. And the answer is a minimum 4dB loss budget. Further, most carriers have expressed a preference for a 5dB loss budget for their 2km reach telecom interfaces, as well as some IDC operators.


Chris

 

From: Scott Kipp [mailto:skipp@xxxxxxxxxxx]
Sent: Tuesday, January 08, 2013 9:49 AM
To: Chris Cole; STDS-802-3-100GNGOPTX@xxxxxxxxxxxxxxxxx
Subject: RE: SMF Ad Hoc

 

Chris,

 

I suggest that we specify our single-mode links in a similar way that they have been defined in IEEE 802.3-2012.

 

For 10GBASE-LR, the channel insertion loss is defined as:

Notes below Table 52-14:

c. The channel insertion loss is calculated using the maximum distance specified in Table 52–11 and cabled optical fiber

attenuation of 0.4 dB/km at 1310 nm plus an allocation for connection and splice loss given in 52.14.2.1.

 

52.14.2.1 states:

The maximum link distances for single-mode fiber are calculated based on an allocation of 2 dB total

connection and splice loss at 1310 nm for 10GBASE-L, and 2 dB for 30 km total connection and splice loss

at 1550 nm for 10GBASE-E.

 

Even for 100GBASE-LR4 and 40GBASE-LR4, the connection insertion loss is:

88.11.2.1 Connection insertion loss

The maximum link distance is based on an allocation of 2 dB total connection and splice loss.

 

So the usual standard for single-mode Ethernet links is 2dB of connection insertion loss and we should continue to specify single-mode links with this connection loss unless there is a good reason to change.

 

The exception to this way of defining connection insertion loss is 40GBASE-FR.  Since 40GBASE-FR was designed to use the same module for VSR2000-3R2 applications as well, the connection loss was increased to 3.0dB and the channel insertion loss was defined as 4dB.  This was a reasonable variation from the normal specification methodology to interoperate with other telecom equipment.  Since the 100GBASE-nR4 solution does not have this requirement for compatibility with VSR, the 802.3bm task force does not need to carry this costly requirement of a 3.0 dB connection loss and 4.0dB loss budget into 100GBASE-nR4.

 

The standard even calls out how 40GBASE-FR is defined differently from other Ethernet standards:

89.6.4 Comparison of power budget methodology

This clause uses the budgeting methodology that is used for application VSR2000-3R2 in ITU-T G.693

[Bx1], which is different from the methodology used in other clauses of this standard (e.g., Clause 38,

Clause 52, Clause 86, Clause 87, Clause 88).

 

For 802.3bm, we should define the channel insertion loss as distance * loss/distance + connection loss.

 

For a 500m solution, the channel insertion loss would likely be: 0.5km * 0.4dB/km + 2.0dB of connection loss = 2.2dB.

For a 2km solution, the channel insertion loss would likely be: 2 km * 0.4dB/km + 2.0dB of connection loss = 2.8dB.

 

Kind regards,

Scott

 

 

From: Chris Cole [mailto:chris.cole@xxxxxxxxxxx]
Sent: Tuesday, January 08, 2013 7:55 AM
To: STDS-802-3-100GNGOPTX@xxxxxxxxxxxxxxxxx
Subject: Re: [802.3_100GNGOPTX] SMF Ad Hoc

 

I look forward to hearing the presentations on this today’s SMF Ad Hoc call.

 

However, having previewed the presentations, I continue to be disappointed that we are still discussing reach as if that was the only important application parameter. For example, shen_01_0113_smf only discusses 2km as if that was sufficient to describe the application. There is no mention of loss budget. Further, by only focusing on reach, the presentation perpetuates the myth that somehow the 10km reach is a niche application, and that we have just discovered 2km as an overlooked sweet spot.

 

It is well understood that there are few datacenter reaches that are 10km. What is important about widely used 10km interfaces like 10GE-LR, 40GE-LR4, and 100GE-LR4 is their greater than 6dB loss budget. In most applications, the reach is much less than 10km, but the >6dB loss budget is fully utilized.

 

2km reach has been an important and wide spread application, with both ITU-T and IEEE standardizing on a minimum 4dB loss budget. This means that over the last decade, end users have become accustomed to interfaces labeled 2km supporting a 4dB loss budget, and designed their central offices and datacenters around this. It is not clear why we continue to reinvent the wheel and propose reducing the established 4dB loss budget by fractions of a dB, for example as in vlasov_01_0113_smf to 3.5dB. If we were to deploy such an interface, it will cause problems in existing applications which try to use the new interface and find the supported loss budget less than expected. The new interface will require datacenter link engineering, as opposed to the plug-and-play paradigm that has made Ethernet so successful.

 

When discussing datacenter interfaces, it will be very helpful to always state both the reach and loss budget, for example 500m/2dB, 2km/4dB, or 10km/6dB, or something else. This way, there will be a clear understanding of what application is being addressed.

 

Thank you

 