Roger, Rick,
 
    I am combining the responses together here. Thank you for your input. I will think about this some more.
 
David
----- Original Message -----
Sent: Thursday, May 31, 2001 3:27 PM
Subject: RE: insuring the stability of power delivery

David,
you bring up some good points, and you echo some of my concerns.

First of all, my opinion is that there are 5 different states of operation:

1) Discovery of 25K slope, the behavior is well accepted at this point
        2.8V to 10V delta of 2V min, PD is +/-5%, discovery time is xx ms, etc...
        the max allowed load cap is about 0.7uF (PSE and PD)

2) Classification
        it is optional for both PSE and PD
        it is done at 15V to 20V, and from 5ma to 40ma (roughly) depending on the class
        it is done only after the discovery portion for the protection of legacy devices, hazard matrix, etc...
        the max allowed load cap is also probably about 0.7uF (PSE and PD)

3) Power Ramp Up
        there is some kind of UVLO with hysteresis, Yair's numbers are mostly accepted
        PSE and PD both manage the startup current
        0.5A is the max current for xx ms
        the max cap load is now 50uF, higher values require PD circuitry to buffer (to be defined)

4) Continuous Power Delivery
        the load current is between 10ma and 350ma
        the PD max power is 12.95W, the PSE min available power is 15.4W
        the PSE puts out between 44V and 57V
        I think that we need to add bandwidth of interest and spec the allowed loads, e.g. cap loads

5) Power Ramp Down
        occurs due to unplug after xx ms
        occurs due to an over-current or other fault
        must return to the discovery process before power can be applied again

To start with, these states each contain behavior that is unique to that state,
the behavior is then simplified between different states if possible.


My last email concerned only power ramp up and continuous delivery, not classification.

I agree, I do not think that we can get "perfect" stability, but we should decide on some performance goals.
We do not want a compliant PD to oscillate so that the voltages and current are driven outside of the proper
bounds therefore resulting in the power turning off.
It can be difficult to design a PSE output that is stable into any load, right?
Phase and gain margins are one way to define stability.
We could devise a separate test fixture for both the PSE and PD to test for compliance.

A purely resistive load should be easy, where the min cap is close to zero.
A large cap/res load is rather easy, except for huge cap values.
Again, large cap values are possible if the PD provides the proper load to the PSE.
Constant power loads (negative resistance loads) with caps can be harder to control and specify,
these types will account for most of the loads we will have (IP phones, etc...)

I just want us to figure out what we need to do to guarantee interoperability, otherwise, the standard
may not succeed.

thanks,
- Rick





    -----Original Message-----
    From:   David Kohl [SMTP:dkohl@xxxxxxxxxxxx]
    Sent:   Thursday, May 31, 2001 3:40 AM
    To:     Brooks, Rick [SC5:321:EXCH]; stds-802-3-pwrviamdi
    Subject:        Re: insuring the stability of power delivery

    Rick,
     
        Your questions are all good. But I believe this over laps some what with the classification process. (Or maybe I am just sensitive because of a real world situation that I have seen.)

     
        Recently I have been made aware of a situation at an end user site. The PD, (and I use this term loosely to put it in terms of the groups discussion), equipment was specified as watt load of X watts by Manufacturer A. The power engineering was done for Manufacturer B's equipment. It was determined that a system of Y watts was required to hand X*Z loads. (The system actually had 2*Y capacity) Yet in reality during the start up phase of the system the real requirement for power delivery was 4*Y.

     
        Unofficial investigation showed that indeed Manufacturer A load specification was as stated, except during startup. During start up  the system exhibited a large capacitive characteristics.

    And we all know that caps take time to charge, and draw decreasing currents as they do charge.
    So initially they look like short circuits. In all other ways the PD works very well.
     
        Unspoken here is the reaction of the end user.
     
        This puts me firmly on the side of specifying the behavior of both the PSE and the PD during the start up mode. In addition, (now that I am thinking about this, I was not in St. Louis), should there be some specification for startup during the classification process? (Now I am getting away from the issue.) The point being that System Engineering of the whole Ethernet link could possibly create a system which would run perfectly once it is up. But because of the lack of power up specification would not start. Modeling both the PSE and PD during start up mode would prevent this from occurring.

        Another point. I fully understand the engineering reasons for increasing the cap at the PD. But in the above example this clearly did not help during the start up phase.

     
        So I have a couple of questions.
     
        1)    Do we need perfect stability? Or is it possible that some instability can be acceptable? ( I am defining stability as the change in voltage or current over time.) I would guess that getting perfect stability is not possible. But some low bandwidth instability would be possible without impacting system performance. But where would this instability begin to impact the signaling?

     
        2)    Is there a trade off between instability and cap size, which will allow a minimum size cap to be used?
     
        Thank you for your input.
     
    David Kohl
     
     
     
     

      ----- Original Message -----
      From: Rick Brooks <mailto:ribrooks@xxxxxxxxxxxxxxxxxx>
      To: stds-802-3-pwrviamdi@xxxxxxxx <mailto:stds-802-3-pwrviamdi@xxxxxxxx>
      Sent: Wednesday, May 30, 2001 7:01 PM
      Subject: insuring the stability of power delivery


      Hi,
      I just wanted to voice one concern that I have regarding power ramp up, and continuous power modes.
      I was reminded of this issue when I was simulating the current limits in the PSE and PD and watching
      oscillations on the cable during startup. Yair's Pspice circuit does not have these problems
      due to the fact that there are Op-amps in the current limit feedback loops (i.e. band limited).

      It seems to me that we do not yet have a defined and specified behavior that will insure that the DTE power will be
      delivered in a stable way.
      How do we guarantee that a PD from vendor "A" will not oscillate when connected to a PSE from vendor "B"?
      The PD as an electrical load needs to be dominated by a capacitive reactance.
      I think that we all agree, but this has not yet been specified.

      During power ramp up, either the PSE or PD current limit will be in effect, so we need to specify the behavior
      during power ramp up.

      At the present time, what behavior is specified to insure that the PSE feedback loops,
      either to regulate the output voltage, or to limit the current (protection circuits),
      will not oscillate with the longest UTP cable or the PD?

      It seems that we need to address these issues or we do not have a complete standard.

      Some ideas:
      1) specify the maximum loop bandwidths of the PSE and PD loops so that any such system will always
      behave as a lumped circuit. In other words, spec the loop bandwidth so that it is about 6 to 10
      times smaller than 1/lambda of the maximum length UTP cable.
      We do not want sudden load changes to cause oscillation or ringing, for instance.
      Slew rate helps, but it is a large signal behavior only.

      2) specify a minimum phase margin into a "standard" PD load (whatever that is)

      3) specify a maximum gain at the UTP bandwidth at the longest cable.

      4) both the PSE and PD need to have a specified behavior.


      Any other ideas or discussion on this topic?
      How about you power guys???

      thanks,
      - Rick