- To: "'Donald S. Stewart'" <dsstewart@xxxxxxxxx>, "'R karam'" <rkaram@xxxxxxxxx>, "'Rick Brooks'" <ribrooks@xxxxxxxxxxxxxxxxxx>, "'Schwartz, Peter'" <Peter.Schwartz@xxxxxxxxxx>, "'Dave Dwelley'" <ddwelley@xxxxxxxxxx>, "'Lynch, Brian'" <brian_lynch@xxxxxx>, "'bruce.inn@xxxxxxxxxx'" <bruce.inn@xxxxxxxxxx>, "'Steve Carlson'" <scarlson@xxxxxxxxxxxxx>, "'AvinoamL@xxxxxxxxxxxxxxxxx'" <AvinoamL@xxxxxxxxxxxxxxxxx>
- Subject: [802.3af] Classification currents range
- From: Yair Darshan <YairD@xxxxxxxxxxxxxx>
- Date: Tue, 21 Aug 2001 18:13:02 +0200
- Cc: "'stds-802-3-pwrviamdi@xxxxxxxx'" <stds-802-3-pwrviamdi@xxxxxxxx>
- Sender: owner-stds-802-3-pwrviamdi@xxxxxxxxxxxxxxxxxx
Guys,
It seems that the gaps between currents specified for various classes
of PDs during the classification procedure are too small and may produce
a measurement accuracy issue.
I am suggesting to change Table 3 in the Draft for the following numbers:
Class0 <1.5mA
Class1 8 - 10 ma
Class2 13 - 16 ma
Class3 19 - 23 ma
Class4 27 - 33 ma
Class5 37 - 45 ma
Greater than 49mA: Invalid result, not a PD.
Comments?